#1 EliasB


    New Member

  • Members
  • Pip
  • 2 posts

Posted 17 January 2012 - 04:31 PM


I'd like to know if it's possibel to do any gonfigurations of the XN05 ModBUS modules exept for what's possible to do when programming the PLC. I.e. is it possible to configure any time outs or the amount of information in the response from the module to the client.

I have three XD26 PLC:s with one XN05 module each in a applcation and I get different responses from them when using function code 16 (Write multiple registers). One problem are the "length" bytes in the MBAP header; they does not correspond to the actual data amount transferred from the XN05...

With best regards

Elias Björkelund de Faire

#2 Jesus Miranda

Jesus Miranda

    Forum Savant

  • Authorized Member
  • PipPipPipPipPipPipPip
  • 125 posts

Posted 31 January 2012 - 06:11 PM

Hello Elias.

Sorry, but you can only configure what is available through the M3 Software. There is no way for other parameters on the XN05 module to be changed.